Troubleshooting common issues with your high cost performance ATO 5hp VFD can be streamlined by following a systematic approach. Accurately locate the problem, avoid direct replacement of the machine. Common Fault Codes and Solutions No Display on Power-Up Keypad Symptoms: The VFD keypad shows no diRead more
Troubleshooting common issues with your high cost performance ATO 5hp VFD can be streamlined by following a systematic approach. Accurately locate the problem, avoid direct replacement of the machine.
Common Fault Codes and Solutions
No Display on Power-Up Keypad
Steps to Troubleshoot:
1. Confirm whether the voltage at the RST terminal is normal (measured with a multimeter in AC mode), and check the terminal wiring for short circuits (control board 10V, 24V power supply, etc.).
2. Check that the keypad leads are correct. If not, re-plug the keypad leads or replace the keypad.
3. Measure the control board terminal 10V, 24V to ensure there is voltage. If not, then measure the voltage between GND and +5V to confirm it is 5V.
Common Fault Codes (E-01, E-03)
Steps to Troubleshoot:
1. Check the wiring: Ensure the incoming and outgoing wires are correctly connected, and the cable insulation is good.
2. Remove the motor wires, power down, and power up again. Restore factory settings (set P3.01=10) and re-plug the 26P and 40P ribbon cables.
3. Run the VFD at 50Hz and measure whether the three-phase output voltage is balanced.
Overcurrent Fault (E-09, E-10)
Steps to Troubleshoot:
1. Check if the operating current exceeds the rated current of the VFD and motor.
2. Recheck if there is any external load jamming or insufficient lubrication of the equipment bearings.
3. Adjust the torque or control mode settings (e.g., P0.09, P0.07, P5.04, P9.13) to match the load.
Undervoltage and Overvoltage Faults (E-04, E-05, E-06, E-07)
Steps to Troubleshoot:
1. Confirm the input power supply is correct (e.g., 380V vs. 220V).
2. Measure the voltage at both ends of the P+ and P- busbars to see if they are normal (around DC300V for 220V systems and around DC540V for 380V systems).
3. If the busbar detection circuit is faulty, recalibrate it using precise fine-tuning.
Output Imbalance Fault (E-12)
Steps to Troubleshoot:
1. Remove the UVW motor wire and run the VFD to measure whether the output voltage is balanced.
2. Measure the three-phase insulation and ground insulation of the UVW motor.
3. Check if the parameters of the VFD are set reasonably.
Additional Tips
Wiring and Parameter Settings: Ensure that the wiring is correct and the parameters are set according to the load requirements. ATO emphasizes the importance of matching the motor model with the VFD’s nameplate power and verifying the selection.
Motor and System Abnormalities: Check for any damage to the motor casing, bad insulation, or stuck shafts. Also, ensure that the customer’s machinery is not jammed and that the peripheral control lines are functioning correctly.
By following these troubleshooting steps and tips from ATO, you can effectively diagnose and resolve common issues with your durable ATO 5hp VFD. If problems persist, consider consulting the user manual or contacting ATO’s technical support for further assistance.